Hello all!
I'm planning a detached backyard drum studio (new construction, room-within-a-room design) and want to sanity-check my wall assembly options before committing. I've done some research but the theoretical transmission loss calculations I'm running seem pessimistic compared to what I see in successful builds online. Some background on my project:
Project Goals
- Primary use: Acoustic drum practice and recording
- Location: Residential backyard in Texas USA, ~30 ft from property line
- Foundation: Concrete slab (no floating floor planned)
- Roof/ceiling: TBD - haven't finalized assembly yet
- Noise constraint: City ordinance limits:
- Daytime (7 AM - 10 PM): 70 dB(A) / 80 dB(C) at property line
- Nighttime (10 PM - 7 AM): 50 dB(A) / 60 dB(C) at property line
- I plan to play during daytime only, so targeting the 70 dB(A) / 80 dB(C) limit
- Source level: Acoustic drums typically produce 105-115 dBC (I'm using 110 dBC as my reference)
- Required isolation: ~40 dB minimum to meet daytime limit, targeting 55-60 dB for safety margin
The Concern
I'm particularly worried about kick drum frequencies (40-80 Hz). My understanding is that double-wall systems have a mass-spring-mass resonance frequency where isolation drops, and I want to make sure whichever assembly I choose doesn't have its resonance frequency right in the kick drum range.
Options I'm Considering
Approach A: Decoupled Double Stud Wood Frame (most common approach I've found in the US)
- Outer leaf: 2×4 studs + 2× 5/8" drywall (~21.4 kg/m² / 4.4 lbs/ft²)
- Inner leaf: 2×4 studs + 2× 5/8" drywall (~21.4 kg/m² / 4.4 lbs/ft²)
- Cavity: 8" total (3.5" outer stud + 1" gap + 3.5" inner stud), filled with mineral wool
- Estimated resonance: ~41 Hz
Approach B: CMU (concrete block) Outer Shell + Decoupled Wood Inner Frame
- Outer leaf: 8" CMU solid grouted (~420 kg/m² / 86 lbs/ft²)
- Inner leaf: 2×4 studs + 2× 5/8" drywall (~21.4 kg/m² / 4.4 lbs/ft²)
- Cavity: 4" air gap with mineral wool
- Estimated resonance: ~42 Hz
Approach C: Decoupled Double Brick Shells
- Outer leaf: Single wythe brick (~195 kg/m² / 40 lbs/ft²)
- Inner leaf: Single wythe brick (~195 kg/m² / 40 lbs/ft²)
- Cavity: 4" air gap
- Estimated resonance: ~19 Hz
My Calculations
I built a simple transmission loss calculator using the London/Sharp mass-air-mass formulas. The graph attached shows estimated TL across the frequency spectrum for each approach.
According to the graph, Approach A (double-stud wood) shows a resonance dip right around 40 Hz, while B performs similarly but with more mass (thus more isolation across the board), and C's resonance is well below the kick drum range.
But here's my confusion: Countless drum studios have been built successfully with double-stud wood construction (Approach A), and Rod Gervais specifically recommends it. What is missing from these theoretical calculations?
It seems that the isolation right at the kick drum frequencies for approach A are basically negligible. It doesn't look like it would drop that specific frequency to my target.
Questions
1. For those who've built studios with double-stud wood: did you have issues with kick drum isolation, or does it work fine in practice?
2. Given my 70 dB daytime limit, would Approach A be sufficient, or should I consider the heavier masonry options?
3. What am I missing here? There has to be something here given all the studios I've seen built with this approach with great results.
Thanks for any insights!
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line)
-
MisterBuildMan
- New Member
- Posts: 6
- Joined: Sun, 2026-Jan-25, 18:10
- Location: Austin, Texas
-
MisterBuildMan
- New Member
- Posts: 6
- Joined: Sun, 2026-Jan-25, 18:10
- Location: Austin, Texas
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line)
Oops, I think I may have forgotten to attach the image in my original post. Here's the graph comparing TL across the frequency spectrum for the three approaches I mentioned above.
- Soundman2020
- Site Admin
- Posts: 914
- Joined: Thu, 2019-Sep-19, 22:58
- Location: Santiago, Chile
- Contact:
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line)
Hi there, and Welcome to the Forum!
Congratulations on your project! It sounds VERY nice. So here's just a few comments, in no particular order:
In fact, the "A" scale on your sound level meter very roughly approximates the 40-phon Equal Loudness Curve, while the "C" scale very roughly approximates the 100-phon Equal Loudness Curve. Take a look at those curves, think about your frequencies and levels, and you'll likely find that either of your "B" and "C" construction options would work just fine, and maybe even "A" if you beef up the mass some more and put plenty of suitable insulation in the air gap. Green Glue can be your fried here: more effective than extra layers of drywall, and especially at low frequencies. Here's why: The truth about Green Glue
You might find that option "B" would be really good, especially if you increase the cavity depth to 6" and put a layer of Green Glue between your two layers of drywall.
Hope that helps a bit!
- Stuart -
Congratulations on your project! It sounds VERY nice. So here's just a few comments, in no particular order:
Great! You probably don't need a floating floor. Here's why: Floating your floor: How and why... and why not.- Foundation: Concrete slab (no floating floor planned)
Cool! Lucky you! Those are unusually high levels, so it should not be too hard to get the isolation you need.- Noise constraint: City ordinance limits:
- Daytime (7 AM - 10 PM): 70 dB(A) / 80 dB(C) at property line
Sounds about right. To put that in perspective, typical house walls give around 30 dB, which isn't very much. 40 dB is about twice as good (subjectively: half as loud). 60 dB is about as much as you can hope for in a typical home studio, unless you have very deep pockets. 50 to 55 is reasonable and achievable on a typical good budget.- Required isolation: ~40 dB minimum to meet daytime limit, targeting 55-60 dB for safety margin
All isolation barriers have some type of natural resonance. The advantage of a double wall MSM system is that you can tune it to your needs. Ideally, the tuned frequency should be half of the lowest frequency that you need to isolate. So if you need to isolate the typical kick at around 80 Hz, the tuned frequency of your wall should be below 40 Hz. If you need to isolate 6-string bass guitar, which goes down to around 32 Hz, then you'd need a tuned frequency of 16 Hz or lower. Etc.I'm particularly worried about kick drum frequencies (40-80 Hz). My understanding is that double-wall systems have a mass-spring-mass resonance frequency where isolation drops, and I want to make sure whichever assembly I choose doesn't have its resonance frequency right in the kick drum range.
Nice work! Those graphs look realistic, and doing a calculator like that isn't easy. Good job! If you'd care to share that tool, I'd be happy to post it here on the form for everyone to use, if they wish, obviously giving credit to you. Of course, if you don't want to share, that's fine too! That took a lot of work to get right, I'm sure.I built a simple transmission loss calculator using the London/Sharp mass-air-mass formulas. The graph attached shows estimated TL across the frequency spectrum for each approach.
Right! And note that you have two dips in the response for that. Not exactly sure what that second dip is (around 300 Hz, it seems): it could be any of several things. My guess would be a coincidence dip. But that reduces your overall isolation. I would not go with double-stud walls using that construction layout where drums are involved, unless you beef up both leaves considerably.According to the graph, Approach A (double-stud wood) shows a resonance dip right around 40 Hz, while B performs similarly but with more mass (thus more isolation across the board), and C's resonance is well below the kick drum range.
I think you'll find that Rod uses more mass and greater air gaps on his drum studios. You also don't seem to be taking into account the insulation in the gap: that's a major part of the MSM equation. Maybe you are, but you didn't mention it in the graphs. That's important to know. The key metrics there are the GFR (Gas Flow Resistivity) of the specific insulation material, and the thickness of that material. You get maximum isolation when the cavity is 100% filled with suitable insulation.But here's my confusion: Countless drum studios have been built successfully with double-stud wood construction (Approach A), and Rod Gervais specifically recommends it. What is missing from these theoretical calculations?
In addition to the above (insulation), you are probably not considering Messrs. Fletcher and Munson. They did a number of experiments on human hearing way back, and discovered that we are not as sensitive to low frequency sounds as we are to mids and highs, and the sensitivity varies based on the level of the sound. They developed a set of curves that show this sensitivity, and those are know a the "Fletch-Munson curves". Later, other folks did additional work, and revised those curves. They are now referred to as the "equal loudness curves". Basically, we just aren't very good at hearing low frequency sound at a low dB level. We can hear mids very well at the same dB level. So, even though your isolation might not look so good for kicks and floor toms, as measured in our numbers, when you take into account the equal loudness curves, they probably won't be heard be actual people, as long as they are reasonably quiet.3. What am I missing here? There has to be something here given all the studios I've seen built with this approach with great results.
In fact, the "A" scale on your sound level meter very roughly approximates the 40-phon Equal Loudness Curve, while the "C" scale very roughly approximates the 100-phon Equal Loudness Curve. Take a look at those curves, think about your frequencies and levels, and you'll likely find that either of your "B" and "C" construction options would work just fine, and maybe even "A" if you beef up the mass some more and put plenty of suitable insulation in the air gap. Green Glue can be your fried here: more effective than extra layers of drywall, and especially at low frequencies. Here's why: The truth about Green Glue
You might find that option "B" would be really good, especially if you increase the cavity depth to 6" and put a layer of Green Glue between your two layers of drywall.
Hope that helps a bit!
- Stuart -
-
MisterBuildMan
- New Member
- Posts: 6
- Joined: Sun, 2026-Jan-25, 18:10
- Location: Austin, Texas
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line)
Thanks for your detailed response Stuart
Following up on some of your comments
I haven't found (yet) a ton of data on this. As in, how much folks typically spend on their studios. Now I know not a single studio is the same, and it all very much differs by country, materials used, and a myriad of other variables, but what would you consider a "typical good budget"? I was quoted ~$80k USD by a studio designer and was a bit surprised (for a 16'x20' building, "simple" single room backyard drum studio / shed). I was hoping to fall somewhere in the half point of that
I have not yet gotten to the point where I've calculated materials / labor costs but its certainly coming up.
Good advice! Seems like I definitely need to beef up my assemblies.
Thank you! I must say I didn't do a ton other than piggy-back off of other people's hard work and studies. However, I've made a point to add this to my to-do list. I'd love to contribute back to this forum! I'll let you know when I've made it publicly available.
This is very true -- my calculations currently don't take that into account. I'll need to re-run the numbers with this in place and see where we land.
Good info on the equal loudness curve, I did not know that was a thing and will make sure to dig in.
In my humble opinion it does seem that either approaches B or C would greatly outperform approach A. However, it does raise more questions and concerns. In the case of either approach B or C, I'm not quite sure how we would make a roof assembly of similar mass such that the roof does not become the weak link. Approaches B and C are also much less DIY friendly, and thus costs rise. It also seems more difficult to bring in electric, HVAC, etc... Rod's book briefly dedicates about half a page to masonry construction specifically for studio design, saying that it's definitely feasible but doesn't go into anywhere as much detail as he does with his wood frame approaches, which is a bummer!
I really enjoyed reading this post. For years I've known about Green Glue, but was always on the fence about it. Too many differing opinions from many people on places like Youtube. The data in this post makes it clear that it can actually be very useful.
---
Thank you Stuart, this does help a lot. I'm going to revisit my numbers and see if I can't come up with a better assembly. Which by the way, if there's any assemblies for Approach A that cross your mind in terms of simplicity and effectiveness -- just shout. I don't want to be reinventing the wheel, I'm sure this has been done successfully countless times with simple materials.
50 to 55 is reasonable and achievable on a typical good budget.
I haven't found (yet) a ton of data on this. As in, how much folks typically spend on their studios. Now I know not a single studio is the same, and it all very much differs by country, materials used, and a myriad of other variables, but what would you consider a "typical good budget"? I was quoted ~$80k USD by a studio designer and was a bit surprised (for a 16'x20' building, "simple" single room backyard drum studio / shed). I was hoping to fall somewhere in the half point of that
Ideally, the tuned frequency should be half of the lowest frequency that you need to isolate.
Good advice! Seems like I definitely need to beef up my assemblies.
Nice work! Those graphs look realistic, and doing a calculator like that isn't easy. Good job! If you'd care to share that tool, I'd be happy to post it here on the form for everyone to use, if they wish, obviously giving credit to you. Of course, if you don't want to share, that's fine too! That took a lot of work to get right, I'm sure.
Thank you! I must say I didn't do a ton other than piggy-back off of other people's hard work and studies. However, I've made a point to add this to my to-do list. I'd love to contribute back to this forum! I'll let you know when I've made it publicly available.
You also don't seem to be taking into account the insulation in the gap: that's a major part of the MSM equation. Maybe you are, but you didn't mention it in the graphs. That's important to know
This is very true -- my calculations currently don't take that into account. I'll need to re-run the numbers with this in place and see where we land.
Good info on the equal loudness curve, I did not know that was a thing and will make sure to dig in.
You might find that option "B" would be really good, especially if you increase the cavity depth to 6" and put a layer of Green Glue between your two layers of drywall.
In my humble opinion it does seem that either approaches B or C would greatly outperform approach A. However, it does raise more questions and concerns. In the case of either approach B or C, I'm not quite sure how we would make a roof assembly of similar mass such that the roof does not become the weak link. Approaches B and C are also much less DIY friendly, and thus costs rise. It also seems more difficult to bring in electric, HVAC, etc... Rod's book briefly dedicates about half a page to masonry construction specifically for studio design, saying that it's definitely feasible but doesn't go into anywhere as much detail as he does with his wood frame approaches, which is a bummer!
Green Glue can be your fried here: more effective than extra layers of drywall, and especially at low frequencies. Here's why: The truth about Green Glue
I really enjoyed reading this post. For years I've known about Green Glue, but was always on the fence about it. Too many differing opinions from many people on places like Youtube. The data in this post makes it clear that it can actually be very useful.
---
Thank you Stuart, this does help a lot. I'm going to revisit my numbers and see if I can't come up with a better assembly. Which by the way, if there's any assemblies for Approach A that cross your mind in terms of simplicity and effectiveness -- just shout. I don't want to be reinventing the wheel, I'm sure this has been done successfully countless times with simple materials.
-
MisterBuildMan
- New Member
- Posts: 6
- Joined: Sun, 2026-Jan-25, 18:10
- Location: Austin, Texas
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line)
Ok, just playing around with the calculator and honing in on a few more options that stick to the wood framing construction method, so essentially variants of approach A...
Approach A remains our baseline -- just 2 layers of 5/8 drywall (which by the way, as I was reading through this original option I realized this does not make sense, as drywall cannot be used as the outer leaf since it's not structural. Keeping this option as a baseline however). This has a resonance frequency of ~41Hz, right on the lower end of the kick drum.
Approach A2 adds considerably more mass: the outer leaf is 3 layers of 3/4 OSB and the inner layer is 1 layer of 3/4 OSB and 2 layers of 5/8 drywall with an 8" cavity. This manages to move the resonance frequency down to ~32Hz.
A3 is the same in term of materials as A2, but the cavity is increased to 12". This change moves the resonance frequency down to ~26Hz.
And in terms of TL loss, massive improvement:
- Approach A: 2.9dB TL @ 40Hz
- Approach B: 18.4dB TL @ 40Hz
- Approach C: 24.3dB TL @ 40Hz
This calculation still does not take into account the effects of insulation within the cavity OR green glue between layers. It also does not take into account the great increase in $$$
I figure that's my next step. Well, two things really:
1) Understand the relation between TL and $ for these approaches. Ideally we reduce overengineering as much as possible and we pick the solution that meets the goal while minimizing $ spend. I figure this may be a tricky thing to calculate but not impossible.
2) I also need to understand the effect of _distance_ and transmission loss. Right now these numbers are all well and good but if my target legally is 30ft away at the boundary line, I wonder how that 30ft distance helps attenuate TL. Same for my neighbors, the nearest one being about 70ft away.
So many questions, so many different options! I'll post updates as I come across findings!
Approach A remains our baseline -- just 2 layers of 5/8 drywall (which by the way, as I was reading through this original option I realized this does not make sense, as drywall cannot be used as the outer leaf since it's not structural. Keeping this option as a baseline however). This has a resonance frequency of ~41Hz, right on the lower end of the kick drum.
Approach A2 adds considerably more mass: the outer leaf is 3 layers of 3/4 OSB and the inner layer is 1 layer of 3/4 OSB and 2 layers of 5/8 drywall with an 8" cavity. This manages to move the resonance frequency down to ~32Hz.
A3 is the same in term of materials as A2, but the cavity is increased to 12". This change moves the resonance frequency down to ~26Hz.
And in terms of TL loss, massive improvement:
- Approach A: 2.9dB TL @ 40Hz
- Approach B: 18.4dB TL @ 40Hz
- Approach C: 24.3dB TL @ 40Hz
This calculation still does not take into account the effects of insulation within the cavity OR green glue between layers. It also does not take into account the great increase in $$$
I figure that's my next step. Well, two things really:
1) Understand the relation between TL and $ for these approaches. Ideally we reduce overengineering as much as possible and we pick the solution that meets the goal while minimizing $ spend. I figure this may be a tricky thing to calculate but not impossible.
2) I also need to understand the effect of _distance_ and transmission loss. Right now these numbers are all well and good but if my target legally is 30ft away at the boundary line, I wonder how that 30ft distance helps attenuate TL. Same for my neighbors, the nearest one being about 70ft away.
So many questions, so many different options! I'll post updates as I come across findings!
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line)
I'm building a (band)practice room in my backyard, in which I want to setup my Pearl GLX kit with 22" and 24" bass drums. I'm 3 months into my build (will open a separate topic someday) and I've not done any calculations on TL of my construction but done estimations and go for the best options that are possible within my limits of budget and the space available. The $1.000.000 question remains; will it be enough for what I want? Which is to play drums anytime of the day without disturbing the neighborhood. My build is your option A with the outer leaf consisting of 2 layers of 18mm OSB and the inside leaf is 18mm OSB with 12,5mm drywall, on a concrete slab. Each leaf has it's own solid core door and laminated glass window.
Yesterday I stumbled upon this video: https://youtu.be/F-yfn5pifbE?si=FE-yIXQnhuUVutDy If the measurements are anything to go by, it gives me hope that my sound proofing results will be even better. Even though he calls it a room-in-a-room, the walls seem to be attached to the outer layer walls and he used resilient channel for the ceiling. Rest of the details are pretty vague as he wants to sell his course on how to build a soundproof studio. Just to be clear; I'm not using his method or approve it, as I haven't and will not buy it. His measurement and recording of the sound leakage was interesting to me at least.
For my build I'm using the info found on this forum and before that the John Sayers, Gearspace and of course the studio builders bible a.k.a. Build It Like The Pro's. There's a wealth of information given by knowledgeable people like Rod, Andre, Glenn and of course Stuart, just to name a few.
Yesterday I stumbled upon this video: https://youtu.be/F-yfn5pifbE?si=FE-yIXQnhuUVutDy If the measurements are anything to go by, it gives me hope that my sound proofing results will be even better. Even though he calls it a room-in-a-room, the walls seem to be attached to the outer layer walls and he used resilient channel for the ceiling. Rest of the details are pretty vague as he wants to sell his course on how to build a soundproof studio. Just to be clear; I'm not using his method or approve it, as I haven't and will not buy it. His measurement and recording of the sound leakage was interesting to me at least.
For my build I'm using the info found on this forum and before that the John Sayers, Gearspace and of course the studio builders bible a.k.a. Build It Like The Pro's. There's a wealth of information given by knowledgeable people like Rod, Andre, Glenn and of course Stuart, just to name a few.
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line)
generally speaking, if you're doing the fully decoupled walls - do a properly decoupled ceiling - i.e. the inner walls are load bearing and the ceiling is part of that overall mass boundary. resilient channel or clips + hat channel are less effective. consider making the exterior boundary with something more massive 2x OSB is still fairly "light" imho. on the inside - OSB on the frames then 2x 15mm type X drywall (fire resistant) will be a better choice. given things need to be sealed - plan your openings (doors, windows etc) and hvac as soon as you have an idea of the floorplan. you need fresh air exchange (temperature, moisture, pollen, dirt, etc), probably cooling and heating.
-
MisterBuildMan
- New Member
- Posts: 6
- Joined: Sun, 2026-Jan-25, 18:10
- Location: Austin, Texas
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line)
Hey gullfo thanks for chiming in!
I'm a bit confused about your comment on the ceiling and inner walls being load bearing.
I do plan on making a fully decoupled ceiling, and was planning on following the inside out ceiling approach (viewtopic.php?f=12&t=50). I believe with this approach resilient channel or clips is not even required. And I'll certainly consider making the exterior boundary more massive.
Do you have any thoughts on having different masses across leaves? Or do you also suggest beefing up the internal leaf? I'm currently thinking 3 layers of OSB but haven't made a final decision yet.
I'm still very early stages into the actual design of the whole structure -- I've been looking at permitting in my area and all that. Certainly the most convoluted part seems to be the HVAC. Cooling is most certainly a requirement since Texas summers can be pretty brutal.
I'm a bit confused about your comment on the ceiling and inner walls being load bearing.
I do plan on making a fully decoupled ceiling, and was planning on following the inside out ceiling approach (viewtopic.php?f=12&t=50). I believe with this approach resilient channel or clips is not even required. And I'll certainly consider making the exterior boundary more massive.
Do you have any thoughts on having different masses across leaves? Or do you also suggest beefing up the internal leaf? I'm currently thinking 3 layers of OSB but haven't made a final decision yet.
I'm still very early stages into the actual design of the whole structure -- I've been looking at permitting in my area and all that. Certainly the most convoluted part seems to be the HVAC. Cooling is most certainly a requirement since Texas summers can be pretty brutal.
-
- Similar Topics
- Statistics
- Last post
-
-
Rural Earth Wall Studio - Using Existing Slab Attachment(s)
by trispembo » Tue, 2026-Jan-13, 00:22 » in RECORDING STUDIO DESIGN -
Replies: 0
Views: 671 -
by trispembo
View the latest post
Tue, 2026-Jan-13, 00:22
-
-
-
Seeking Advice on Drum Room Location
by skankhunt42 » Wed, 2026-Mar-11, 03:01 » in RECORDING STUDIO DESIGN -
Replies: 0
Views: 176 -
by skankhunt42
View the latest post
Wed, 2026-Mar-11, 03:01
-
-
-
Floating floor meets isolated Wall... Attachment(s)
by killerjoe » Fri, 2025-Jul-18, 11:19 » in RECORDING STUDIO CONSTRUCTION -
Replies: 1
Views: 63512 -
by gullfo
View the latest post
Fri, 2025-Jul-18, 18:32
-
-
-
Just Another Garage Studio Attachment(s)
by bradvuv » Sat, 2025-Aug-16, 01:40 » in RECORDING STUDIO DESIGN -
Replies: 6
Views: 96829 -
by bradvuv
View the latest post
Tue, 2025-Aug-19, 01:41
-
Who is online
Users browsing this forum: No registered users and 26 guests