Multi-purpose Music/Home Theater/Recording Studio
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
No, it's the space above the two storage that I'm going to fill with Rockwool for using as bass traps.
The soffits are filled with wool but closed with 5/8 drywall to soundproof the air ducts.
Stef
The soffits are filled with wool but closed with 5/8 drywall to soundproof the air ducts.
Stef
Multi-purpose Music/Home Theater/Recording Studio
if you use a silencer on the wall penetrations for the supply and return, you don't need to soundproof the ducts. and if they're flex duct, even better. the soffits (if they were soft) would absorb a lot, and adding some hard plates etc along the sides and/or bottom to keep things from being completely flat, you would get a really good benefit...
even hard ducts, fully damped, would be ok. the key for the air system is low velocity and low noise vents. silencers for penetration between spaces to attenuate inter-room sound transfers.
even hard ducts, fully damped, would be ok. the key for the air system is low velocity and low noise vents. silencers for penetration between spaces to attenuate inter-room sound transfers.
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Here's how the ducts are installed:
In the left soffit, there's the return grille preceded by approximately 3 feet of acoustical flex and approximately 2 feet of hard duct at the wall outlet.
In the right soffit, there are 3 supply grilles (blue = hard, green = flex). At the wall exit, there is a Y then 3 feet of acoustic flex before the first grille. The hard duct continues about 4 feet to the second Y then about 6 feet of flex before the second grille. The hard duct continues about 5 feet then about 8 feet of flex before the third grille.
Acoustic flexible ducts are used here to reduce the velocity (and therefore the noise) before reaching the grilles.
I filled the soffits with fiberglass.
Q1: Are you saying I should cover the front of the soffits with fabric (the side where the grilles are) instead of drywall?
(For the bottom, I need to use drywall to support the recessed lights and drivers)
Q2: Are you saying I should put drywall only where there is a grill or light, and put fabric for the rest of the soffits?
Stef
In the left soffit, there's the return grille preceded by approximately 3 feet of acoustical flex and approximately 2 feet of hard duct at the wall outlet.
In the right soffit, there are 3 supply grilles (blue = hard, green = flex). At the wall exit, there is a Y then 3 feet of acoustic flex before the first grille. The hard duct continues about 4 feet to the second Y then about 6 feet of flex before the second grille. The hard duct continues about 5 feet then about 8 feet of flex before the third grille.
Acoustic flexible ducts are used here to reduce the velocity (and therefore the noise) before reaching the grilles.
I filled the soffits with fiberglass.
gullfo wrote:Source of the post the soffits (if they were soft) would absorb a lot
Q1: Are you saying I should cover the front of the soffits with fabric (the side where the grilles are) instead of drywall?
(For the bottom, I need to use drywall to support the recessed lights and drivers)
gullfo wrote:Source of the post and adding some hard plates etc along the sides and/or bottom to keep things from being completely flat
Q2: Are you saying I should put drywall only where there is a grill or light, and put fabric for the rest of the soffits?
Stef
Multi-purpose Music/Home Theater/Recording Studio
since you already have the drywall on the bootom - i'd leave that, but i would cover the side face with cloth.
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Hi, before reading your post of October 23, I had already almost finished the drywall on the sides...
...fortunately, it didn't cost almost anything because I used most of the leftovers from the walls. I only bought a 4x10 sheet.
The drywall is installed in sections of 48 inches or less, so it's very easy to remove everything. I'll keep and number the pieces, just in case.
If I left the drywall (instead of fabric), I would have to tape and mud the joints (green lines) and install 90° metal corner beads (blue lines).
But if I put fabric, how do I proceed with plastering?
Here's what I'm thinking: I screw the corner beads as planned so I can plaster and paint the bottom of the soffits. I put the fabric on frames (as I would for an acoustic panel) so that the frame goes all the way to the ceiling and to the bottom of the soffits. Choose a fabric that is white and matches the white of the paint. I hang the frames on the soffits as I would for an acoustic panel. Place the frames so that the joints between two frames are as small as possible. I cut the fabric where there is a return or supply and I place the finishing grille.
Does this make sense?
Stef
...fortunately, it didn't cost almost anything because I used most of the leftovers from the walls. I only bought a 4x10 sheet. If I left the drywall (instead of fabric), I would have to tape and mud the joints (green lines) and install 90° metal corner beads (blue lines).
But if I put fabric, how do I proceed with plastering?
Here's what I'm thinking: I screw the corner beads as planned so I can plaster and paint the bottom of the soffits. I put the fabric on frames (as I would for an acoustic panel) so that the frame goes all the way to the ceiling and to the bottom of the soffits. Choose a fabric that is white and matches the white of the paint. I hang the frames on the soffits as I would for an acoustic panel. Place the frames so that the joints between two frames are as small as possible. I cut the fabric where there is a return or supply and I place the finishing grille.
Does this make sense?
Stef
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Finally, I found that drywall helps cut the sound of the ducts where the duct enters the studio. So, I'm going to put about 12 feet of fabric just in the middle of the soffits.
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
I can finally give an update. I had to take a short break from the studio because I had to supervise some home renovations. However, the work has still progressed a bit since my last post. Here is :
and some photos :
Next steps: cutting the materials for the back wall 2x4 frame, the cloud and the rolling supports for the office partitions. The idea is to get as much of the dusty work done as possible before painting. Winter arrived earlier this year, and it's not very appealing to set up outside to saw wood...if I have the choice.
As usual, all comments are welcome.
Stef
- Finished putting the Rockwool in the bass traps above the storage (about 30 cubic feet of Rockwool in each...or $250 worth of Rockwool each
). To cut the Rockwool, I used an old ceramic kitchen knife I had kept. Much more effective for this purpose than my utility knife! - installed storage doors
- Finished installing the drywall on the soffits and storage
- installed casing and metal corners
- mineral wool was placed in the threshold of the sliding doors
- sealing the inside corners of sliding doors (backer rods and urethane)
- plastering (by a contractor...1 week)
- cutting the moldings (they will be painted the same color as the wall and doors)
- TV delivery
and some photos :
Next steps: cutting the materials for the back wall 2x4 frame, the cloud and the rolling supports for the office partitions. The idea is to get as much of the dusty work done as possible before painting. Winter arrived earlier this year, and it's not very appealing to set up outside to saw wood...if I have the choice.
As usual, all comments are welcome.
Stef
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Thank you so much, Glenn! As always, I really appreciate your comments and encouragement...this project is quite an adventure! My friend thought it would take us 3 months!
Progress over the last few days:
- Sliding door baseboard
- Glued 1/4-inch plywood to the blue Dow insulation at the bottom of the back wall, carefully replicating the 2x6 stud marks to attach the TV brackets.
- Built the 2x4 frame for the back wall (this wall will be filled with 3.5-inch Rockwool, covered with black fabric and vertical slats, and will house the 85-inch TV). The horizontal 2x4s are screwed into the furring strips beneath the two layers of drywall. However, for the two vertical pieces supporting the TV, we drilled three holes halfway through the 2x4 and used 6" screws to reach the 2x6 stud. We also placed a screw at the top and bottom of each piece.
We made a first frame out of 1x3s to cover the soffits with fabric, but it was too thick.
I want a frame that's flush with the 5/8" drywall on each side. So I bought a sheet of 5/8" OSB to make a new frame, and the result is still pretty good.
We simply stapled the pieces together (on both sides) so it was just strong enough to allow the fabric to be stapled. The problem was how to attach the frame to the soffit. Since these frames don't need to be removed, and to avoid any vibration, we decided to nail them (with an air nailer and finishing nails), hoping the hole wouldn't show. We did a test, but the hole in the fabric is visible. The solution I found was to put a white thumbtack over the nail.
If anyone has a better idea for fixing these frames, it would be most welcome!
Stef
Progress over the last few days:
- Sliding door baseboard
- Glued 1/4-inch plywood to the blue Dow insulation at the bottom of the back wall, carefully replicating the 2x6 stud marks to attach the TV brackets.
- Built the 2x4 frame for the back wall (this wall will be filled with 3.5-inch Rockwool, covered with black fabric and vertical slats, and will house the 85-inch TV). The horizontal 2x4s are screwed into the furring strips beneath the two layers of drywall. However, for the two vertical pieces supporting the TV, we drilled three holes halfway through the 2x4 and used 6" screws to reach the 2x6 stud. We also placed a screw at the top and bottom of each piece.
We made a first frame out of 1x3s to cover the soffits with fabric, but it was too thick.
I want a frame that's flush with the 5/8" drywall on each side. So I bought a sheet of 5/8" OSB to make a new frame, and the result is still pretty good.
We simply stapled the pieces together (on both sides) so it was just strong enough to allow the fabric to be stapled. The problem was how to attach the frame to the soffit. Since these frames don't need to be removed, and to avoid any vibration, we decided to nail them (with an air nailer and finishing nails), hoping the hole wouldn't show. We did a test, but the hole in the fabric is visible. The solution I found was to put a white thumbtack over the nail.
If anyone has a better idea for fixing these frames, it would be most welcome!
Stef
Multi-purpose Music/Home Theater/Recording Studio
one approach is to use "cabinet" latches - the plastic kind that snap into each other. maybe six of those pairs per panel would keep it secure.
something like this: https://www.amazon.com/uxcell-Furniture ... B07VYG97FD or similar like https://www.amazon.com/Cupboard-Plastic ... B0CWXW7G9Y
something like this: https://www.amazon.com/uxcell-Furniture ... B07VYG97FD or similar like https://www.amazon.com/Cupboard-Plastic ... B0CWXW7G9Y
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Don't worry, I'm still alive!
Actually, I haven't had much time to update my project, but work is progressing well. I'm taking the time to do this update before taking a few weeks off.
We built the frames for the two 4x8 clouds. Then, before painting, we positioned them on the floor opposite where they would be mounted on the ceiling to locate the ceiling slats. We inserted screws, which will be replaced with eye bolts to hold the clouds in place. For each screw, we used a string with a weight to pinpoint the exact locations for attaching 2x4 reinforcements to the clouds for the hooks.
The two clouds were very useful long before they were installed on the ceiling...I used them to paint the baseboards and the slats of the slatted wall!
All the painting is finished and the recessed lights are installed in the soffits.
About the frames covered with fabric to cover the soffits, we finally decided to nail them in place so we could adjust them to the ceiling and the bottom of the soffits as closely as possible. The nail holes aren't very noticeable; you really have to get close and look closely. And the end result is quite acceptable (fabric vs. painted drywall). Before nailing them, I installed pieces vertically to prevent the wool from touching the fabric. The red arrows indicate the fabric sections (6 feet long each).
The back wall is finished and the TV is mounted on its wall bracket. Several hours of work were required to sand, stain and varnish the 32 slats! Previously, we ran all the necessary cabling along the back wall, passing through the storage areas.
(to be continued in the next post...)
We built the frames for the two 4x8 clouds. Then, before painting, we positioned them on the floor opposite where they would be mounted on the ceiling to locate the ceiling slats. We inserted screws, which will be replaced with eye bolts to hold the clouds in place. For each screw, we used a string with a weight to pinpoint the exact locations for attaching 2x4 reinforcements to the clouds for the hooks.
The two clouds were very useful long before they were installed on the ceiling...I used them to paint the baseboards and the slats of the slatted wall!
All the painting is finished and the recessed lights are installed in the soffits.
About the frames covered with fabric to cover the soffits, we finally decided to nail them in place so we could adjust them to the ceiling and the bottom of the soffits as closely as possible. The nail holes aren't very noticeable; you really have to get close and look closely. And the end result is quite acceptable (fabric vs. painted drywall). Before nailing them, I installed pieces vertically to prevent the wool from touching the fabric. The red arrows indicate the fabric sections (6 feet long each).
The back wall is finished and the TV is mounted on its wall bracket. Several hours of work were required to sand, stain and varnish the 32 slats! Previously, we ran all the necessary cabling along the back wall, passing through the storage areas.
(to be continued in the next post...)
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
We installed the power outlets for the control room area and the outlets on the side walls.
The baseboards at the bottom of the walls have been installed and painted. In the storage units, I glued and painted MDF panels to protect the walls.
I installed an MDF panel, which I painted the same color as the wall, for access to the mini-split piping. I used the same material to cover the ERV and radiant floor system in the gym.
(to be continued in the next post...)
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
I applied two coats of sealant to the floor.
We installed the furniture that I kept from the renovation of the bathroom of the house. I also kept an old desk for the workshop area and had a similar counter made for the other side.
We installed a Video Blink Doorbell and a Blink camera in the gym. Both have a motion detector and send notifications via the app on my phone.
That's it. That's where we're at. Work will resume in a few weeks with the finalization and installation of the clouds. As always, any comments are welcome.
Stef
We installed the furniture that I kept from the renovation of the bathroom of the house. I also kept an old desk for the workshop area and had a similar counter made for the other side.
We installed a Video Blink Doorbell and a Blink camera in the gym. Both have a motion detector and send notifications via the app on my phone.
That's it. That's where we're at. Work will resume in a few weeks with the finalization and installation of the clouds. As always, any comments are welcome.
Stef
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Hello,
Here is an update on the work done since my last post. We first completed the construction and installation of the 2 clouds.
CLOUDS
We started by drilling holes in the OSB pieces for the recessed fittings. I have a 6-inch hole saw, but it was impossible to use it for drilling the holes because OSB is a very hard material, and as soon as the blade bit into the wood, it was impossible to hold the drill and risked injury. The hole saw was only used to trace a circle on the OSB, and then we cut it out with the oscillating saw.
I drilled 12 holes, each ½ inch in diameter, to allow sound to pass through. I didn't want to make too many so as not to weaken the OSB, but I think I could have made more and used a 1-inch drill bit.
Then we stapled the fabric and put the lights in the holes. (It looks like the fabric isn't opaque enough, but that's because there's a lot of light in the room.) Finally, my friend did the wiring and electrical connections for the 2 lights.
Here is the hardware we used to hang the clouds.
We first removed the screws from the ceiling (those corresponding to the first cloud) and replaced them with eye bolts. But before screwing in the eye bolts, we used a drill bit (with a smaller diameter than the eye bolt) to completely drill through the slat to avoid splitting it when screwing in the eye bolts.
We then screwed the eye bolts onto the cloud, onto the pieces of 2x4 that we had added for this purpose.
We then used four ratchet straps to suspend the cloud and gradually raise it to the ceiling. We first raised it a few feet to facilitate the installation of the insulation and the geotextile fabric. Finally, we raised it to the ceiling (one side at a time) and replaced the straps with quick links and two chain links, resulting in a distance of 8 inches between the top of the cloud and the ceiling.
(to be continued in the next post...)
Here is an update on the work done since my last post. We first completed the construction and installation of the 2 clouds.
CLOUDS
We started by drilling holes in the OSB pieces for the recessed fittings. I have a 6-inch hole saw, but it was impossible to use it for drilling the holes because OSB is a very hard material, and as soon as the blade bit into the wood, it was impossible to hold the drill and risked injury. The hole saw was only used to trace a circle on the OSB, and then we cut it out with the oscillating saw.
I drilled 12 holes, each ½ inch in diameter, to allow sound to pass through. I didn't want to make too many so as not to weaken the OSB, but I think I could have made more and used a 1-inch drill bit.
Then we stapled the fabric and put the lights in the holes. (It looks like the fabric isn't opaque enough, but that's because there's a lot of light in the room.) Finally, my friend did the wiring and electrical connections for the 2 lights.
Here is the hardware we used to hang the clouds.
We first removed the screws from the ceiling (those corresponding to the first cloud) and replaced them with eye bolts. But before screwing in the eye bolts, we used a drill bit (with a smaller diameter than the eye bolt) to completely drill through the slat to avoid splitting it when screwing in the eye bolts.
We then screwed the eye bolts onto the cloud, onto the pieces of 2x4 that we had added for this purpose.
We then used four ratchet straps to suspend the cloud and gradually raise it to the ceiling. We first raised it a few feet to facilitate the installation of the insulation and the geotextile fabric. Finally, we raised it to the ceiling (one side at a time) and replaced the straps with quick links and two chain links, resulting in a distance of 8 inches between the top of the cloud and the ceiling.
(to be continued in the next post...)
-
- Similar Topics
- Statistics
- Last post
-
-
Big Beautiful Basement Studio
by micahmicahmicah » Tue, 2026-Feb-10, 17:55 » in RECORDING STUDIO DESIGN -
Replies: 3
Views: 259583 -
by Soundman2020
View the latest post
Tue, 2026-Mar-24, 22:00
-
-
-
Rural Earth Wall Studio - Using Existing Slab
by trispembo » Tue, 2026-Jan-13, 00:22 » in RECORDING STUDIO DESIGN -
Replies: 0
Views: 64288 -
by trispembo
View the latest post
Tue, 2026-Jan-13, 00:22
-
-
-
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line) Attachment(s)
by MisterBuildMan » Sun, 2026-Jan-25, 22:17 » in RECORDING STUDIO DESIGN -
Replies: 8
Views: 1200285 -
by gullfo
View the latest post
Sat, 2026-Mar-21, 13:08
-
Who is online
Users browsing this forum: No registered users and 92 guests