Multi-purpose Music/Home Theater/Recording Studio

Document your build here: All about your walls, ceilings, doors, windows, HVAC, and (gasp!) floated floors...
goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#16

Postby goodwater » Mon, 2025-May-12, 08:44

Yes, « the bolt and washer attached to the top plate also the bolt that runs through the pad and into the slats » but before inserting the bolt we inserted a piece of rubber hose up to the top of the slat, so the bolt and the washer do not touch the wood (the washer crushes the piece of hose that protrudes on the slat and on the bottom of the top plate) as we did to fix the walls on the exterior wall.

Rubber hose 1.JPG

Rubber hose 2.JPG


Does this change your recommendation?

Stef



User avatar
gullfo
Senior Member
Posts: 793
Joined: Fri, 2021-Jun-25, 14:50
Location: Panama City Beach, FL USA

Multi-purpose Music/Home Theater/Recording Studio

#17

Postby gullfo » Wed, 2025-May-14, 19:26

in looking closer - you have a bolt with a washer contacting the lower plate, the bolt threads are wrapped with hose, a pad between the plate and ceiling slats, a hose through the opening in the slat, then a washer and nut on the bolt. the members are still coupled because the bolt transfers from the plate to the slat at the washer connecting point - what you want is a decoupling of the washer as well. see Kinetics Noise KSR 25 assembly for the concept.

on sealing the wall-ceiling gap - typically your sheathing on the walls and ceiling are staggered to around 1/4" separation on each layer and those are sealed. the depth of (typcially) 1/2" plywood/osb + 2x 5/8" type-x drywall would give you 1-3/4" thick "edges".

example decoupled wall and ceiling layers0002.jpg



goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#18

Postby goodwater » Tue, 2025-Jul-08, 12:41

Hi,

The work is progressing well. The gym is almost finished, and we're about to begin work on the studio. Here's what's been done since my last update in this (construction) thread.

  • Plastering and paint
  • Installation of PVC door and window moldings
  • Necessary improvement of the radiant heating system (unforeseen cost of $1500)
  • Installation of the sliding (retractable) toilet door

toilet1.JPG

toilet2.JPG


  • closing the top of the wall with a layer of 5/8 OSB and 3 layers of 5/8 gypsum so that the last layer touches the ceiling (well sealed after each layer)

top.JPG


  • installation of the ERV and preheat coil above the toilet
  • installation of soffit exhaust vent to exaust stale aire and soffit intake vent for the supply of fresh air from outdoors (done by my HVAC contractor).

hvac1.JPG

hvac2.JPG

hvac3.JPG


  • installation of ventilation ducts (gym only)
  • holes in the drywall to run the conduit into the studio and another for a 3-inch pipe to run the electrical wires through. Conduits and pipe are sealed from each side.
    1. preheat coil
    2. fresh air to the studio (flexible acoustical duct before enter the wall)
    3. fresh air to the gym
    4. stale air from the studio and gym (the hole is on the other side of the gym)

hvac4.JPG

hvac5.JPG

hvac6.JPG


  • I sealed the wall corners and the top as best I could. Fiberglass in the top and fiberglass/backer rods (red arrows)/gwb 5/8/sealant in the corners.

wall1.JPG

wall2.JPG


  • We built the frame to hide the HVAC and electrical installations. We can close it when we're done running wires to the studio.

frame1.JPG

frame2.JPG


  • I applied 2 coats of sealer to the floor (to protect and facilitate cleaning)

floor.JPG


  • Construction, painting and installation of baseboards, moldings and speaker shelves.
  • Installation of suspended ceiling (by a contractor)
  • Installation of the fresh air and exhaust air diffusers (before each diffuser, the duct terminates in 3 feet of 6-inch flexible acoustic duct)
  • Installation of the 2 light fixtures, TV and Stereo wall mounts (I used surface PVC electrical outlets and sealed the hole in the outlet and on the other side of the wall)

gym1.JPG

gym2.JPG

gym3.JPG


  • I bought a router and a friend of mine came to make the connectors in the house and the gym. Wifi up and running!
  • Cleaning the studio and moving things from the studio to the gym. Studio (and more interesting) part ready to start ! (but first I will continue soon on the Design Forum)

There you go. I know it's not perfect, but we're doing our best.
Feel free to comment, whether positive or negative. Thank you.



goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#19

Postby goodwater » Tue, 2025-Sep-02, 13:52

Here's the work we've done since my last update. We've made a lot of progress and I'll probably need more than one post.

I sealed the bottom of the first wall and we put the fiberglass wool in this wall.

Bottom plate.JPG


We nailed the slats every 24 inches on the walls studs and every 16 inches on the ceiling trusses. We put an extra slat 16 inches from the ceiling in preparation for building the soffits.

Wall.JPG

Ceiling.JPG


We laid the first layer of drywall. We actually had to alternate between the ceiling and the walls because there were a lot of things to move as we went along.

We screwed the first layer of drywall to the ceiling (thank goodness I had the good idea to buy a drywall lift...). As I installed it, I placed the neoprene squares every 12 inches (unless otherwise specified) for each screw. I bought rolls of self-adhesive neoprene on Amazon and cut them into 2-inch strips. I cut the squares as I installed them. However, for the joints I made 2x4 inch rectangles. A few joints weren't perfect so I filled them with sealant.

Neoprene1.JPG

Neoprene2.JPG

Neoprene3.JPG

Neoprene4.JPG

Joint.JPG


In order to screw the neoprene squares properly, I made lines and then dots with a black marker. Same thing for the walls.

Black dots.JPG


I put wool between the top plate and the ceiling (1). Then we installed slats (to form a 90-degree angle) to have a hard base so we could screw the drywall into this corner (2). I also put wool in the corner of the second wall (3). Then I put the drywall the corner.

Wool and slats.JPG

Corner.JPG


We had to cut the drywall to fit into the slats. I'll have to seal it well and the second layer of drywall will go over the slats.

Insertions.JPG


After that I sealed the corners before putting the drywall on the walls.

Backer rod.JPG

Caulk.JPG


We screwed the first layer of drywall onto the walls except the dividing wall because there are still wires to run. Then backer rods and seal.

Wall1.JPG

Wall2.JPG


Before putting the wool in the first wall, I put Putty Pads (which I bought to put around the air duct holes) over the sealant of the wires that go into the gym. I also ran an 8 pair snake to the gym.

Putty Pad.JPG

Snake.JPG


...more to come



goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#20

Postby goodwater » Tue, 2025-Sep-02, 14:10

continuation of my previous post...

As I wrote in my design thread, I decided to install an air conditioner. Before the contractor came, we ran an electrical wire from the panel to the outside by drilling a hole between the two walls. Then my friend installed a circuit breaker box (required by the contractor). I dug a 16x32 inch hole 6 inches deep, filled with compacted stone dust, and placed 2 concrete tiles.

Minisplit1.JPG


The contractor then came to install the piping and the outdoor unit. He will return to install the indoor unit when the wall above the sliding doors is done.

Minisplit2.JPG


We installed the two sliding doors. Beforehand, we decoupled the two walls by cutting the 2x4s. We glued a ¼ plywood to the floor and then laid a layer of neoprene (an old mat that I bought to put under an elliptical).

Sliding1.JPG


Before putting up the second door, we put 2 layers of 5/8 drywall on the walls and ceiling in the space between the doors. The doors are not yet sealed (more details later).

Sliding2.JPG

Sliding3.JPG


After that, we put the second layer of drywall on ceiling and walls by overlapping the joints (I would have preferred to stagger the sheets a little more but it's probably better than not overlapping at all). Then backer rod and caulk after each.

According to my design, I was supposed to screw the second layer only into the first (without touching the slats) but after experimenting with several types of screws it wasn't strong enough. So I decided to use 2-inch screws to screw down to the slats. I might lose a few db but at least I won't be afraid of the ceiling falling on my head.

We're almost done, but we have to wait until we close the second wall before we can finish the drywall. The final sealing is not yet done.

second layer1.JPG

second layer2.JPG

second layer3.JPG


As I always say, if you see any mistakes or things I could have done better, please let me know. I may not be able to make the corrections but it may be useful to other forum readers!

Stef



goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#21

Postby goodwater » Wed, 2025-Sep-03, 13:16

I have 2 questions:

  1. In my design, I screw the second layer every 12 inches, but since I'm now screwing all the way to the slats (with 2-inch screws), I thought it would be enough to screw it every 16 inches, or 28 screws for a 4x8 sheet. Is that enough to properly tighten the second layer to the first?

  2. Yesterday, while searching the forum for an answer to my question 1, I read that it would have been better if I had sealed all the joints in the first layer (plaster or sealant covered with duck tape). Is this a serious mistake and will there be a significant impact on the soundproofing of low frequencies? (About 90% of the joints in the sheets I installed are tight. I put sealant in the less tight ones.)

Thanks!



User avatar
gullfo
Senior Member
Posts: 793
Joined: Fri, 2021-Jun-25, 14:50
Location: Panama City Beach, FL USA

Multi-purpose Music/Home Theater/Recording Studio

#22

Postby gullfo » Wed, 2025-Sep-03, 16:44

it would have been best to run a quick coat of dywall mud on the joins - so maybe do that for the walls.

in generally, if you stagger the screws on 16" then you get approx a screw per 8" so that should be enough. so first layer - 1 1" screw per 16", second layer 1-3/4" (or 2") every 16" stagger with first layer.

a good thing to do is to sheath your framing with 1/2" (or 7/16") plywood / osb and then screw into that (more important if using things like isolation clips and hat channel) so you're not beholden to the joist (or other framing) positions. given the ply or osb is structural material, your framing assembly is more rigid and stronger (for example if you were using metal framing, this would be a huge improvement in strength).



goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#23

Postby goodwater » Thu, 2025-Sep-25, 12:12

Here's the work we've done since my last update.

We have finished installing the insulation in the two walls that separate the studio from the gym. In the workshop area, I ran a wire for an electrical outlet and a CAT5 cable for an internet connection. Above the doors, you can see the pipes for the indoor air conditioning unit.

Wool1.JPG

Wool2.JPG

Wool3.JPG


I routed the wires for the ERV and radiant floor controls inside the 2x4 wall framing so that the controls would be located on the front side of the doors, instead of on the small side wall.

Wires.JPG


We screwed the first layer of drywall into place, I sealed the joints with sealant and covered them with tape. Working around the pipes and the 2x4 studs above the doors required some precision cutting of the drywall... Then I added backer rods and sealant in the corners and along the bottom of the walls.

drywall_1.JPG

drywall_2.JPG

drywall_3.JPG

drywall_4.JPG

drywall_5.JPG

drywall_6.JPG

drywall_7.JPG

drywall_8.JPG

backer rod.JPG

Seal.JPG


more to come...



goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#24

Postby goodwater » Thu, 2025-Sep-25, 12:20

...continuation of my previous post

For the second layer, we laid the sheets horizontally to simplify covering the seams. We still need to finish the sections around the pipes. We started framing the box above the doors so we can install the indoor unit. The contractor came to install it yesterday. I will cover it completely for the duration of the work to prevent dust from entering the unit.

drywall_9.JPG

Minisplit_1.JPG

Minisplit_2.JPG


For sealing the door frame on the studio side, I could use a 1/2-inch backer rod and sealant. Then, 5/8-inch drywall will be installed over that.

Door_ExtGap.JPG


On the inside of this door (between the 2 doors), the opening is larger and would require a ¾-inch backer rod. Instead, I thought I would fill the gap with polyurethane sealant for doors and windows (instead of wool) and then seal with sealant. Then, I would attach a trim piece to cover the edge where the PVC panel meets the wall.

Door_IntGap.JPG


For the floor, I'm going to seal the edges with sealant, then I'll lay down plywood and a floating floor to bring it up to the same level as the doors.

Door_IntGap2.JPG


Is this a good way to seal the doors?



goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#25

Postby goodwater » Sun, 2025-Sep-28, 13:54

So, what I'm planning to do to seal the doors, is that okay or could I do it better?



User avatar
gullfo
Senior Member
Posts: 793
Joined: Fri, 2021-Jun-25, 14:50
Location: Panama City Beach, FL USA

Multi-purpose Music/Home Theater/Recording Studio

#26

Postby gullfo » Mon, 2025-Sep-29, 18:33

are the doors on separate frames or a single frame assembly? if the former - on the covering of the frames - leave a gap and seal it - back rod and caulk to reduce any structural transfer. if it's a single frame assembly, just go ahead and cover. on the side - use a soft foam to fill or if a single frame, back rod, caulk and a finish layer (drywall wood etc).
on the floor - same as walls - keep disconnect if your doors are on paired separate frames, if not, go ahead to make flush.



goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#27

Postby goodwater » Wed, 2025-Oct-01, 15:03

Thanks Glenn. The doors are on separate frames.

After thoroughly protecting the indoor unit, we finished applying the second layer of drywall in the corners (around the ductwork, not yet sealed). I installed backer rods and applied sealant to seal the door frame on the studio side, and then we finished by applying the 5/8" drywall.

Door1.JPG

Conduits.JPG


We started constructing the right storage area and soffit using 2x3 lumber. To prevent touching the sealant while working, I covered it with tape. I marked the locations of the recessed lights and ventilation grilles with paint tape (the green squares and rectangles in the photo) according to the plan, so I knew where not to place the 2x3 pieces. :)

storage.JPG

soffit_1.JPG

tape on sealant.JPG

soffit_2.JPG

soffit_3.JPG


Here is the plan (the ventilation grilles are not correctly positioned in this version):

plan.JPG
plan.JPG (43.01 KiB) Viewed 26227 times
plan.JPG
plan.JPG (43.01 KiB) Viewed 26227 times



User avatar
gullfo
Senior Member
Posts: 793
Joined: Fri, 2021-Jun-25, 14:50
Location: Panama City Beach, FL USA

Multi-purpose Music/Home Theater/Recording Studio

#28

Postby gullfo » Wed, 2025-Oct-08, 16:37

depending on the air ducts sizes, you might make the vents larger to reduce possible noise



goodwater
Active Member
Posts: 75
Joined: Sun, 2022-May-08, 22:45
Location: Canada, Saguenay (Quebec province)

Multi-purpose Music/Home Theater/Recording Studio

#29

Postby goodwater » Wed, 2025-Oct-22, 18:53

Hello...Glenn! ;)
Here's the work we've done since my last update.

We first completed the soffit and storage structure. Before building the soffits, I plastered the part covered by the soffits (wall and ceiling), about 16 inches.

Plastrage soffit.JPG

soffit1.JPG

soffit2.JPG


Then we installed drywall underneath the soffits, drilled holes for the recessed lights, and installed only the junction boxes with integrated drivers. However, we temporarily plugged in all the recessed lights to make sure they worked properly.

soffit3.JPG

soffit4.JPG

boxes.JPG


Next, I sealed the vent pipe and the electrical wire pipe with sealant and Putty Pad. If I had to do it again, I would seal the pipes and install the ducts (holding them in some way) BEFORE building the soffits because it was very difficult to work and put the tape on the ducts.

seal.JPG


Then we installed the air ducts: one exhaust air intake grille on one side and 3 fresh air grilles on the other. The 6 inch pipes terminate in 4x10 inch grille. Before reaching the grilles, I put at least 3 feet of flexible acoustic tubing. I placed the air calibration keys aligned with the recessed holes so that I could reach them after closing the soffits. I placed 2 layers of mineral wool to lay the ducts and electrical wires to avoid any unwanted vibrations in the soffits. The ducts will be completely covered with wool to cut the sound as much as possible.

duct1.JPG

duct3.JPG

duct2.JPG


Tomorrow my HVAC contractor is coming to turn on the ERV and calibrate the system. After that, I can finish installing the drywall on the soffits.



User avatar
gullfo
Senior Member
Posts: 793
Joined: Fri, 2021-Jun-25, 14:50
Location: Panama City Beach, FL USA

Multi-purpose Music/Home Theater/Recording Studio

#30

Postby gullfo » Wed, 2025-Oct-22, 20:32

ok, so you're not going to leverage the soffit space for additional absorption?




  • Similar Topics
    Statistics
    Last post

Who is online

Users browsing this forum: No registered users and 92 guests