Yes, « the bolt and washer attached to the top plate also the bolt that runs through the pad and into the slats » but before inserting the bolt we inserted a piece of rubber hose up to the top of the slat, so the bolt and the washer do not touch the wood (the washer crushes the piece of hose that protrudes on the slat and on the bottom of the top plate) as we did to fix the walls on the exterior wall.
Does this change your recommendation?
Stef
Does this change your recommendation?
Stef
Multi-purpose Music/Home Theater/Recording Studio
in looking closer - you have a bolt with a washer contacting the lower plate, the bolt threads are wrapped with hose, a pad between the plate and ceiling slats, a hose through the opening in the slat, then a washer and nut on the bolt. the members are still coupled because the bolt transfers from the plate to the slat at the washer connecting point - what you want is a decoupling of the washer as well. see Kinetics Noise KSR 25 assembly for the concept.
on sealing the wall-ceiling gap - typically your sheathing on the walls and ceiling are staggered to around 1/4" separation on each layer and those are sealed. the depth of (typcially) 1/2" plywood/osb + 2x 5/8" type-x drywall would give you 1-3/4" thick "edges".
on sealing the wall-ceiling gap - typically your sheathing on the walls and ceiling are staggered to around 1/4" separation on each layer and those are sealed. the depth of (typcially) 1/2" plywood/osb + 2x 5/8" type-x drywall would give you 1-3/4" thick "edges".
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Hi,
The work is progressing well. The gym is almost finished, and we're about to begin work on the studio. Here's what's been done since my last update in this (construction) thread.
There you go. I know it's not perfect, but we're doing our best.
Feel free to comment, whether positive or negative. Thank you.
The work is progressing well. The gym is almost finished, and we're about to begin work on the studio. Here's what's been done since my last update in this (construction) thread.
- Plastering and paint
- Installation of PVC door and window moldings
- Necessary improvement of the radiant heating system (unforeseen cost of $1500)
- Installation of the sliding (retractable) toilet door
- closing the top of the wall with a layer of 5/8 OSB and 3 layers of 5/8 gypsum so that the last layer touches the ceiling (well sealed after each layer)
- installation of the ERV and preheat coil above the toilet
- installation of soffit exhaust vent to exaust stale aire and soffit intake vent for the supply of fresh air from outdoors (done by my HVAC contractor).
- installation of ventilation ducts (gym only)
- holes in the drywall to run the conduit into the studio and another for a 3-inch pipe to run the electrical wires through. Conduits and pipe are sealed from each side.
- preheat coil
- fresh air to the studio (flexible acoustical duct before enter the wall)
- fresh air to the gym
- stale air from the studio and gym (the hole is on the other side of the gym)
- I sealed the wall corners and the top as best I could. Fiberglass in the top and fiberglass/backer rods (red arrows)/gwb 5/8/sealant in the corners.
- We built the frame to hide the HVAC and electrical installations. We can close it when we're done running wires to the studio.
- I applied 2 coats of sealer to the floor (to protect and facilitate cleaning)
- Construction, painting and installation of baseboards, moldings and speaker shelves.
- Installation of suspended ceiling (by a contractor)
- Installation of the fresh air and exhaust air diffusers (before each diffuser, the duct terminates in 3 feet of 6-inch flexible acoustic duct)
- Installation of the 2 light fixtures, TV and Stereo wall mounts (I used surface PVC electrical outlets and sealed the hole in the outlet and on the other side of the wall)
- I bought a router and a friend of mine came to make the connectors in the house and the gym. Wifi up and running!
- Cleaning the studio and moving things from the studio to the gym. Studio (and more interesting) part ready to start ! (but first I will continue soon on the Design Forum)
There you go. I know it's not perfect, but we're doing our best.
Feel free to comment, whether positive or negative. Thank you.
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Here's the work we've done since my last update. We've made a lot of progress and I'll probably need more than one post.
I sealed the bottom of the first wall and we put the fiberglass wool in this wall.
We nailed the slats every 24 inches on the walls studs and every 16 inches on the ceiling trusses. We put an extra slat 16 inches from the ceiling in preparation for building the soffits.
We laid the first layer of drywall. We actually had to alternate between the ceiling and the walls because there were a lot of things to move as we went along.
We screwed the first layer of drywall to the ceiling (thank goodness I had the good idea to buy a drywall lift...). As I installed it, I placed the neoprene squares every 12 inches (unless otherwise specified) for each screw. I bought rolls of self-adhesive neoprene on Amazon and cut them into 2-inch strips. I cut the squares as I installed them. However, for the joints I made 2x4 inch rectangles. A few joints weren't perfect so I filled them with sealant.
In order to screw the neoprene squares properly, I made lines and then dots with a black marker. Same thing for the walls.
I put wool between the top plate and the ceiling (1). Then we installed slats (to form a 90-degree angle) to have a hard base so we could screw the drywall into this corner (2). I also put wool in the corner of the second wall (3). Then I put the drywall the corner.
We had to cut the drywall to fit into the slats. I'll have to seal it well and the second layer of drywall will go over the slats.
After that I sealed the corners before putting the drywall on the walls.
We screwed the first layer of drywall onto the walls except the dividing wall because there are still wires to run. Then backer rods and seal.
Before putting the wool in the first wall, I put Putty Pads (which I bought to put around the air duct holes) over the sealant of the wires that go into the gym. I also ran an 8 pair snake to the gym.
...more to come
I sealed the bottom of the first wall and we put the fiberglass wool in this wall.
We nailed the slats every 24 inches on the walls studs and every 16 inches on the ceiling trusses. We put an extra slat 16 inches from the ceiling in preparation for building the soffits.
We laid the first layer of drywall. We actually had to alternate between the ceiling and the walls because there were a lot of things to move as we went along.
We screwed the first layer of drywall to the ceiling (thank goodness I had the good idea to buy a drywall lift...). As I installed it, I placed the neoprene squares every 12 inches (unless otherwise specified) for each screw. I bought rolls of self-adhesive neoprene on Amazon and cut them into 2-inch strips. I cut the squares as I installed them. However, for the joints I made 2x4 inch rectangles. A few joints weren't perfect so I filled them with sealant.
In order to screw the neoprene squares properly, I made lines and then dots with a black marker. Same thing for the walls.
I put wool between the top plate and the ceiling (1). Then we installed slats (to form a 90-degree angle) to have a hard base so we could screw the drywall into this corner (2). I also put wool in the corner of the second wall (3). Then I put the drywall the corner.
We had to cut the drywall to fit into the slats. I'll have to seal it well and the second layer of drywall will go over the slats.
After that I sealed the corners before putting the drywall on the walls.
We screwed the first layer of drywall onto the walls except the dividing wall because there are still wires to run. Then backer rods and seal.
Before putting the wool in the first wall, I put Putty Pads (which I bought to put around the air duct holes) over the sealant of the wires that go into the gym. I also ran an 8 pair snake to the gym.
...more to come
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
continuation of my previous post...
As I wrote in my design thread, I decided to install an air conditioner. Before the contractor came, we ran an electrical wire from the panel to the outside by drilling a hole between the two walls. Then my friend installed a circuit breaker box (required by the contractor). I dug a 16x32 inch hole 6 inches deep, filled with compacted stone dust, and placed 2 concrete tiles.
The contractor then came to install the piping and the outdoor unit. He will return to install the indoor unit when the wall above the sliding doors is done.
We installed the two sliding doors. Beforehand, we decoupled the two walls by cutting the 2x4s. We glued a ¼ plywood to the floor and then laid a layer of neoprene (an old mat that I bought to put under an elliptical).
Before putting up the second door, we put 2 layers of 5/8 drywall on the walls and ceiling in the space between the doors. The doors are not yet sealed (more details later).
After that, we put the second layer of drywall on ceiling and walls by overlapping the joints (I would have preferred to stagger the sheets a little more but it's probably better than not overlapping at all). Then backer rod and caulk after each.
According to my design, I was supposed to screw the second layer only into the first (without touching the slats) but after experimenting with several types of screws it wasn't strong enough. So I decided to use 2-inch screws to screw down to the slats. I might lose a few db but at least I won't be afraid of the ceiling falling on my head.
We're almost done, but we have to wait until we close the second wall before we can finish the drywall. The final sealing is not yet done.
As I always say, if you see any mistakes or things I could have done better, please let me know. I may not be able to make the corrections but it may be useful to other forum readers!
Stef
As I wrote in my design thread, I decided to install an air conditioner. Before the contractor came, we ran an electrical wire from the panel to the outside by drilling a hole between the two walls. Then my friend installed a circuit breaker box (required by the contractor). I dug a 16x32 inch hole 6 inches deep, filled with compacted stone dust, and placed 2 concrete tiles.
The contractor then came to install the piping and the outdoor unit. He will return to install the indoor unit when the wall above the sliding doors is done.
We installed the two sliding doors. Beforehand, we decoupled the two walls by cutting the 2x4s. We glued a ¼ plywood to the floor and then laid a layer of neoprene (an old mat that I bought to put under an elliptical).
Before putting up the second door, we put 2 layers of 5/8 drywall on the walls and ceiling in the space between the doors. The doors are not yet sealed (more details later).
After that, we put the second layer of drywall on ceiling and walls by overlapping the joints (I would have preferred to stagger the sheets a little more but it's probably better than not overlapping at all). Then backer rod and caulk after each.
According to my design, I was supposed to screw the second layer only into the first (without touching the slats) but after experimenting with several types of screws it wasn't strong enough. So I decided to use 2-inch screws to screw down to the slats. I might lose a few db but at least I won't be afraid of the ceiling falling on my head.
We're almost done, but we have to wait until we close the second wall before we can finish the drywall. The final sealing is not yet done.
As I always say, if you see any mistakes or things I could have done better, please let me know. I may not be able to make the corrections but it may be useful to other forum readers!
Stef
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
I have 2 questions:
Thanks!
- In my design, I screw the second layer every 12 inches, but since I'm now screwing all the way to the slats (with 2-inch screws), I thought it would be enough to screw it every 16 inches, or 28 screws for a 4x8 sheet. Is that enough to properly tighten the second layer to the first?
- Yesterday, while searching the forum for an answer to my question 1, I read that it would have been better if I had sealed all the joints in the first layer (plaster or sealant covered with duck tape). Is this a serious mistake and will there be a significant impact on the soundproofing of low frequencies? (About 90% of the joints in the sheets I installed are tight. I put sealant in the less tight ones.)
Thanks!
Multi-purpose Music/Home Theater/Recording Studio
it would have been best to run a quick coat of dywall mud on the joins - so maybe do that for the walls.
in generally, if you stagger the screws on 16" then you get approx a screw per 8" so that should be enough. so first layer - 1 1" screw per 16", second layer 1-3/4" (or 2") every 16" stagger with first layer.
a good thing to do is to sheath your framing with 1/2" (or 7/16") plywood / osb and then screw into that (more important if using things like isolation clips and hat channel) so you're not beholden to the joist (or other framing) positions. given the ply or osb is structural material, your framing assembly is more rigid and stronger (for example if you were using metal framing, this would be a huge improvement in strength).
in generally, if you stagger the screws on 16" then you get approx a screw per 8" so that should be enough. so first layer - 1 1" screw per 16", second layer 1-3/4" (or 2") every 16" stagger with first layer.
a good thing to do is to sheath your framing with 1/2" (or 7/16") plywood / osb and then screw into that (more important if using things like isolation clips and hat channel) so you're not beholden to the joist (or other framing) positions. given the ply or osb is structural material, your framing assembly is more rigid and stronger (for example if you were using metal framing, this would be a huge improvement in strength).
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Here's the work we've done since my last update.
We have finished installing the insulation in the two walls that separate the studio from the gym. In the workshop area, I ran a wire for an electrical outlet and a CAT5 cable for an internet connection. Above the doors, you can see the pipes for the indoor air conditioning unit.
I routed the wires for the ERV and radiant floor controls inside the 2x4 wall framing so that the controls would be located on the front side of the doors, instead of on the small side wall.
We screwed the first layer of drywall into place, I sealed the joints with sealant and covered them with tape. Working around the pipes and the 2x4 studs above the doors required some precision cutting of the drywall... Then I added backer rods and sealant in the corners and along the bottom of the walls.
more to come...
We have finished installing the insulation in the two walls that separate the studio from the gym. In the workshop area, I ran a wire for an electrical outlet and a CAT5 cable for an internet connection. Above the doors, you can see the pipes for the indoor air conditioning unit.
I routed the wires for the ERV and radiant floor controls inside the 2x4 wall framing so that the controls would be located on the front side of the doors, instead of on the small side wall.
We screwed the first layer of drywall into place, I sealed the joints with sealant and covered them with tape. Working around the pipes and the 2x4 studs above the doors required some precision cutting of the drywall... Then I added backer rods and sealant in the corners and along the bottom of the walls.
more to come...
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
...continuation of my previous post
For the second layer, we laid the sheets horizontally to simplify covering the seams. We still need to finish the sections around the pipes. We started framing the box above the doors so we can install the indoor unit. The contractor came to install it yesterday. I will cover it completely for the duration of the work to prevent dust from entering the unit.
For sealing the door frame on the studio side, I could use a 1/2-inch backer rod and sealant. Then, 5/8-inch drywall will be installed over that.
On the inside of this door (between the 2 doors), the opening is larger and would require a ¾-inch backer rod. Instead, I thought I would fill the gap with polyurethane sealant for doors and windows (instead of wool) and then seal with sealant. Then, I would attach a trim piece to cover the edge where the PVC panel meets the wall.
For the floor, I'm going to seal the edges with sealant, then I'll lay down plywood and a floating floor to bring it up to the same level as the doors.
Is this a good way to seal the doors?
For the second layer, we laid the sheets horizontally to simplify covering the seams. We still need to finish the sections around the pipes. We started framing the box above the doors so we can install the indoor unit. The contractor came to install it yesterday. I will cover it completely for the duration of the work to prevent dust from entering the unit.
For sealing the door frame on the studio side, I could use a 1/2-inch backer rod and sealant. Then, 5/8-inch drywall will be installed over that.
On the inside of this door (between the 2 doors), the opening is larger and would require a ¾-inch backer rod. Instead, I thought I would fill the gap with polyurethane sealant for doors and windows (instead of wool) and then seal with sealant. Then, I would attach a trim piece to cover the edge where the PVC panel meets the wall.
For the floor, I'm going to seal the edges with sealant, then I'll lay down plywood and a floating floor to bring it up to the same level as the doors.
Is this a good way to seal the doors?
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
So, what I'm planning to do to seal the doors, is that okay or could I do it better?
Multi-purpose Music/Home Theater/Recording Studio
are the doors on separate frames or a single frame assembly? if the former - on the covering of the frames - leave a gap and seal it - back rod and caulk to reduce any structural transfer. if it's a single frame assembly, just go ahead and cover. on the side - use a soft foam to fill or if a single frame, back rod, caulk and a finish layer (drywall wood etc).
on the floor - same as walls - keep disconnect if your doors are on paired separate frames, if not, go ahead to make flush.
on the floor - same as walls - keep disconnect if your doors are on paired separate frames, if not, go ahead to make flush.
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Thanks Glenn. The doors are on separate frames.
After thoroughly protecting the indoor unit, we finished applying the second layer of drywall in the corners (around the ductwork, not yet sealed). I installed backer rods and applied sealant to seal the door frame on the studio side, and then we finished by applying the 5/8" drywall.
We started constructing the right storage area and soffit using 2x3 lumber. To prevent touching the sealant while working, I covered it with tape. I marked the locations of the recessed lights and ventilation grilles with paint tape (the green squares and rectangles in the photo) according to the plan, so I knew where not to place the 2x3 pieces.
Here is the plan (the ventilation grilles are not correctly positioned in this version):
After thoroughly protecting the indoor unit, we finished applying the second layer of drywall in the corners (around the ductwork, not yet sealed). I installed backer rods and applied sealant to seal the door frame on the studio side, and then we finished by applying the 5/8" drywall.
We started constructing the right storage area and soffit using 2x3 lumber. To prevent touching the sealant while working, I covered it with tape. I marked the locations of the recessed lights and ventilation grilles with paint tape (the green squares and rectangles in the photo) according to the plan, so I knew where not to place the 2x3 pieces.
Here is the plan (the ventilation grilles are not correctly positioned in this version):
Multi-purpose Music/Home Theater/Recording Studio
depending on the air ducts sizes, you might make the vents larger to reduce possible noise
-
goodwater
- Active Member
- Posts: 75
- Joined: Sun, 2022-May-08, 22:45
- Location: Canada, Saguenay (Quebec province)
Multi-purpose Music/Home Theater/Recording Studio
Hello...Glenn!
Here's the work we've done since my last update.
We first completed the soffit and storage structure. Before building the soffits, I plastered the part covered by the soffits (wall and ceiling), about 16 inches.
Then we installed drywall underneath the soffits, drilled holes for the recessed lights, and installed only the junction boxes with integrated drivers. However, we temporarily plugged in all the recessed lights to make sure they worked properly.
Next, I sealed the vent pipe and the electrical wire pipe with sealant and Putty Pad. If I had to do it again, I would seal the pipes and install the ducts (holding them in some way) BEFORE building the soffits because it was very difficult to work and put the tape on the ducts.
Then we installed the air ducts: one exhaust air intake grille on one side and 3 fresh air grilles on the other. The 6 inch pipes terminate in 4x10 inch grille. Before reaching the grilles, I put at least 3 feet of flexible acoustic tubing. I placed the air calibration keys aligned with the recessed holes so that I could reach them after closing the soffits. I placed 2 layers of mineral wool to lay the ducts and electrical wires to avoid any unwanted vibrations in the soffits. The ducts will be completely covered with wool to cut the sound as much as possible.
Tomorrow my HVAC contractor is coming to turn on the ERV and calibrate the system. After that, I can finish installing the drywall on the soffits.
Here's the work we've done since my last update.
We first completed the soffit and storage structure. Before building the soffits, I plastered the part covered by the soffits (wall and ceiling), about 16 inches.
Then we installed drywall underneath the soffits, drilled holes for the recessed lights, and installed only the junction boxes with integrated drivers. However, we temporarily plugged in all the recessed lights to make sure they worked properly.
Next, I sealed the vent pipe and the electrical wire pipe with sealant and Putty Pad. If I had to do it again, I would seal the pipes and install the ducts (holding them in some way) BEFORE building the soffits because it was very difficult to work and put the tape on the ducts.
Then we installed the air ducts: one exhaust air intake grille on one side and 3 fresh air grilles on the other. The 6 inch pipes terminate in 4x10 inch grille. Before reaching the grilles, I put at least 3 feet of flexible acoustic tubing. I placed the air calibration keys aligned with the recessed holes so that I could reach them after closing the soffits. I placed 2 layers of mineral wool to lay the ducts and electrical wires to avoid any unwanted vibrations in the soffits. The ducts will be completely covered with wool to cut the sound as much as possible.
Tomorrow my HVAC contractor is coming to turn on the ERV and calibrate the system. After that, I can finish installing the drywall on the soffits.
Multi-purpose Music/Home Theater/Recording Studio
ok, so you're not going to leverage the soffit space for additional absorption?
-
- Similar Topics
- Statistics
- Last post
-
-
Big Beautiful Basement Studio
by micahmicahmicah » Tue, 2026-Feb-10, 17:55 » in RECORDING STUDIO DESIGN -
Replies: 3
Views: 232225 -
by Soundman2020
View the latest post
Tue, 2026-Mar-24, 22:00
-
-
-
Rural Earth Wall Studio - Using Existing Slab
by trispembo » Tue, 2026-Jan-13, 00:22 » in RECORDING STUDIO DESIGN -
Replies: 0
Views: 59427 -
by trispembo
View the latest post
Tue, 2026-Jan-13, 00:22
-
-
-
Sanity check: Wall assembly options for backyard drum studio (targeting 70 dB at property line) Attachment(s)
by MisterBuildMan » Sun, 2026-Jan-25, 22:17 » in RECORDING STUDIO DESIGN -
Replies: 8
Views: 1082269 -
by gullfo
View the latest post
Sat, 2026-Mar-21, 13:08
-
Who is online
Users browsing this forum: No registered users and 74 guests