Stand alone "room in a room" studio build in Orange NSW Australia

Document your build here: All about your walls, ceilings, doors, windows, HVAC, and (gasp!) floated floors...
gearjunk1e
Full Member
Posts: 112
Joined: Sun, 2021-Mar-07, 19:19
Location: Orange Australia

Stand alone "room in a room" studio build in Orange NSW Australia

#61

Postby gearjunk1e » Wed, 2025-Aug-20, 07:52

Very, very long time, no post. :oops:

I’ve been waiting for something exciting to happen to prompt an update but it’s mostly just been “same, same” – the grind of gyprocking (drywalling), insulation and sealant (caulking) in my LIVE ROOM. However, I decided it’s good for motivation to stop, document things and celebrate progress - and hopefully there is something useful in here for someone else. (This post will need to be done in instalments so as to not exceed limits on image uploads.)

So, in between the grind:

I have completed and mounted my 2 LIVE ROOM inner silencer boxes and the 4 plenums. :D The inlet fan (and associated ducting/filter) is installed and I’m part way through completing the outlet side duct work. This will also have a fan pulling air out – in an earlier post I noted that the passive pull in the CONTROL ROOM wasn’t clearing the Co2 at an acceptable rate, so I’ve gone with one fan pushing air in and another pulling out. Once the LIVE ROOM is done, I’ll loop back and install the outlet fan on the CONTROL ROOM as well as the CONTROL ROOM outer door.

LIVE ROOM Wall completion
Nothing ground breaking here but I have observed that every “wrinkle” you have – in my case, column boxing and the ceiling rake adds soooo much time relative to straightforward drywall (gyprock) wall hanging and sealing.

LIVE ROOM Ventilation
With the fans now running on "Low" I'm getting a max of 137 ft/min at the exit from the plenum.

Mounting of outside silencer boxes
Various shots of the mounting of the outer inflow silencer for the LIVE ROOM
A the location - LR external silencer (inlet).jpg
Building the frame
B lifting mechanism.jpg
temporary lifting structure
C top frame LR external silencer (inlet).jpg
D final lift - LR external silencer (inlet).jpg
Lifting into place using drywall lift
D LR external silencer (inlet) in place.jpg
E outside panel - LR external silencer (inlet).jpg
I left the last panel off to keep the weight down
F  LR external silencer (inlet)  - all done.jpg
All done

...and one of the outlet outer silencer
G LR external return silencer in place.jpg

Various shots of the mounting of the inner silencer for the LIVE ROOM;
The drywall lift and acrow props got the job done (with a few straps for safety) :D
A internal silencer (inlet) up.jpg
B internal (inlet) side view.jpg
C Inflow to inlet silencer.jpg
A nightmare getting my hands in and seeing what I was doing - this was pre tape and clamps
D inside silencer (inlet) - frame.jpg
support from
E Outlet silencer up.jpg
F Outlet silencer up.jpg
A shot of the LR ventilation structure
LR outside vent.jpg
Inlet, filter and fan section

...more to come - I've run out of picture capacity in this post



gearjunk1e
Full Member
Posts: 112
Joined: Sun, 2021-Mar-07, 19:19
Location: Orange Australia

Stand alone "room in a room" studio build in Orange NSW Australia

#62

Postby gearjunk1e » Thu, 2025-Aug-21, 23:36

Before I discuss the plenums themselves, I’ll touch on their impact on ceiling construction.

I had a conversation mid 2024 with my engineer about the introducing plenums to slow air speed further. This conversation was prompted by the increase in the load on the ceiling joists. The outcome was that I required some extra strengthening on the joists bearing part of that load. (The frame for the silencers/plenums runs from the wall to the first joist)

This is an example where design changes on the run can/could have a sting in the tail.
I needed to bolt a C section steel purlin to the first timber joists at both ends of the room to increase the load bearing capacity. However, the steel purlin needed to be supported directly by the wall frame and I had progressed the frame and sheeting too far at this point to get the steel purlins to land on the existing wall frame. His solution was to add a vertical supporting stud inside the room under the steel purlin at either end and bolt that stud through the wall sheeting to the frame.

It’s not a disaster but could have been; disaster avoided because, after some discussion, the support for the C section is able to run along the line of the rake under the joists – bolted through to the wall frame. I really didn’t want vertical studs inside the room and continuing the horizontal framing under the joists the whole way around helps me with fixing the fabric cover under the joists/insulation anyway.

While this issue has been solved, I’ve burned a lot of time solving it and executing those plans, whereas had I designed it that way, I’d have run the C section through to the wall frame before sheeting and avoided the work-arounds on the wall behind the silencer to fit the plenums. Solved – but I reckon it cost me 2 months in extra work time.
C section.jpg
C section full.jpg
20250711_194832.jpg
Here how the support looks
Now to the plenums themselves. I wish I’d settled on this design waay earlier – retro fitting was painful. Only the final plenum was straightforward as I had;
1. Experience; and
2. Enough of a runway adjacent to its final location to be able to lift it up then slide it back to apply sealant before sliding it back into place

Here's some shots of the construction and installation
At the front (inlet)
C1 Plenum constr.jpg
C2 plenum construction.jpg
D plenum placement RHS inner.jpg
RHS inlet
B inner front plenums on.jpg
Front (inlet) done
At the back (outlet)
A collar internal silencer- return.jpg
The collar into which the plenum entry slides
F fancy lift for placement.jpg
organically developed lift!
G context.jpg
E back plenum excellent fit.jpg
centimeter perfect!
H - nearly done.jpg
nearly there!
I plenum - silencer join.jpg
looks like the silencer/plenum is touching the back wall - just the angle

...still more to come



gearjunk1e
Full Member
Posts: 112
Joined: Sun, 2021-Mar-07, 19:19
Location: Orange Australia

Stand alone "room in a room" studio build in Orange NSW Australia

#63

Postby gearjunk1e » Fri, 2025-Aug-22, 09:37

In the last post I forgot the photos from the last plenum
20250711_194814.jpg
20250731_125626.jpg
I did a dry fit - check that the plenum and silencer vents were butting up together
20250811_162209.jpg
I had to cut out a layer of wall to fit the plenum up into the space once I'd added the little collar that butts up against the big one
20250818_111552.jpg
MAJOR CELEBRATION!

Completion of the walls
Slightly out of time sequence but some shots below of the completion of my LIVE ROOM walls. Amazing how you go much faster with experience!
A corner boxing.jpg
Corner boxing
B Corner boxing 2.jpg
B Corner boxing 2.jpg
C Corner boxing 3.jpg
D Col 1 layer 1.jpg
Column layer 1
E Col 2 frame.jpg
Column frame
F Col 2 layer 2.jpg
Column layer 2
G One wall to go!.jpg
One wall to go!
H last wall layer 1.jpg
last wall layer 1
I Makeshift lifting platform 2.jpg
Makeshift lifting platform
J Makeshift lifting platform.jpg
K Template for rakes.jpg
template for cutting rakes
L walls done.jpg
walls done

Some light entertainment
maximum load.jpg
I'm pretty sure I pushed the ute to the max
special guest.jpg
...in the corner ...a special guest. Better than a snake! but it still scared the XXX out of me when I heard the rustling behind the corflute sheet


Still more to come..



gearjunk1e
Full Member
Posts: 112
Joined: Sun, 2021-Mar-07, 19:19
Location: Orange Australia

Stand alone "room in a room" studio build in Orange NSW Australia

#64

Postby gearjunk1e » Fri, 2025-Aug-22, 18:48

The story continues...

Cabling between rooms
I’ve also been busy sealing penetrations for electrical and network cabling – “Big Stretch” for these. I’ve taken, what I think is a conservative approach by opening out the penetrations a bit (per pic), squeezing as much sealant as I can into the gap between the edge of the hole and the conduit but then I’ve added something akin to a flange around the conduit entry allowing me to apply additional thickness of sealant. The “flanges” are just the cut outs from silencer duct holes.
A electrical penetration.jpg
penetration
B electrical penetration.jpg
closer
C electrical penetration pre flange.jpg
shocking pic but big stretch pre flange
D electrical penetration flange.jpg
flange on
E electrical penetration flange with Big Stretch.jpg
finished job
F Keeping elec conduit away from internal wall.jpg
keeping conduit off the inside wall - there is actually a strip of rubber between the conduit and clamp
I also worked out how I’d run the audio and related cabling between the rooms. I have run the conduits and am now sealing the 2nd layer penetrations. I’m using “Big Stretch” on these again. There is probably a smarter way to do it but that's what I did :D
I’m an old school guy and am wiring for analog connections (mostly balanced but a few unbalanced as well) but have also catered for some optical, midi and cat6 cables. I’m running 4 cables per 30mm conduit with draw strings and the longest run through this wall section is just under a metre, so I’m confident I can pull replacements should (when? :lol: ) I need.
A before conduits.jpg
B conduit.jpg
C conduits.jpg
D conduit.jpg
E conduit.jpg
F conduit.jpg
H conduit 8.jpg
I conduit.jpg
J Cabling conduits to be sealed.jpg
K conduits into CR.jpg
control room side
L conduit outlets CR.jpg
close up control side
Where the conduits “emerge”, they will be covered by some DIY cable covers/boxes and I’m going to use putty pads where the cables exit the conduits into the boxes.

...more to come



gearjunk1e
Full Member
Posts: 112
Joined: Sun, 2021-Mar-07, 19:19
Location: Orange Australia

Stand alone "room in a room" studio build in Orange NSW Australia

#65

Postby gearjunk1e » Sat, 2025-Aug-23, 05:40

The opus continues….

Completion of the Ceiling
I need 3 layers on the ceiling because 2 layers of the 17mm ply I bought has less mass than 2x16mm gyprock (drywall) - which is my wall mass. Some inexperience there – I bought the ply 4 years ago - before I fully understood isolation. But much of layer 1 is left over gyprock from the walls so while time is lost, the cost increment is low.

Early days...
1st sheet of ply.jpg
2nd later front LR c.jpg
Current situation
20250711_194907.jpg
20250711_194912.jpg
20250723_103645.jpg
20250723_103702.jpg

Electrical
My electrician has done the power runs/points and run cabling for lights. I’m using relays extensively to control lights/power/fans in the shed/studio.
20250821_105515.JPG
20250821_105519.JPG
The power points on the column side of the room (in pics) will end up out of sight as I intend to put the cover below in front of the columns but make it slightly wider; then boxing in the power runs on one side and audio cables on the other.
Column covers.png

One more post and we are up to date :D



gearjunk1e
Full Member
Posts: 112
Joined: Sun, 2021-Mar-07, 19:19
Location: Orange Australia

Stand alone "room in a room" studio build in Orange NSW Australia

#66

Postby gearjunk1e » Sat, 2025-Aug-23, 05:48

Next steps
So with just the duct work for the Live Room ventilation return to finish, doors to install, 5 of 24 inside out LIVE ROOM ceiling bays to complete, the final coat of mud on the joins in wall sheeting and the light fixtures to be installed, the end of the construction phase is finally in sight. Then, after the cosmetics, it’s on to the interesting part (for me anyway) – treatment.

To kick off the detailed planning for the treatment of the LIVE ROOM - here’s 2 questions

Question 1
In both my rooms I have an inside out ceiling. I will have a space of ~170-180mm or ~7” to load with insulation. The design follows Stuart’s reference post https://forum.digistar.cl/viewtopic.php?f=12&t=50 ie with strapping, plastic then a fabric cover with trim to hide the staples – nothing original here!
Somewhere on either this forum or John Sayers forum, I have this vague recollection of someone suggesting that in this type of ceiling it might be best to run one layer of slightly higher density insulation with a layer of “pink fluffy” below so as not to suck the life out of the room, given the ceiling is such a large area. (In saying that, the insulation will all be covered by black plastic, preserving a lot of highs).
I can’t find that comment again in my searches but am wondering if either anyone can recall it or even better, offer an experienced opinion on the wisdom (or not) of it.

What I had in mind was Bradford Soundscreen batts – gas flow resistivity falls within range of 10,500 – 13,500 Rays/m.
Bradford SCh.png

What I’ve been using in the gap between rooms and will, by default use in the ceiling space is around 5,000 Rayls/m.
In any event, I won’t be adding any treatment until after I’ve run a base level set of measurements once the door is installed but I did want to get ahead of the game.

Question 2
The other question I have relates to the window between the rooms. I’ve provided for a window in the framing – this gap is currently filled by a temporary single wall to stop dust getting from the LIVE ROOM to the CONTROL ROOM during construction. I’m sure I can build the window frame and install the window but am wondering whether it might be just as effective, cheaper and quicker to use cameras and large screens for visuals between the rooms. I’m just wondering if anyone has experience with this solution versus a real window and/or wisdom to offer here.

Andrew



User avatar
gullfo
Senior Member
Posts: 793
Joined: Fri, 2021-Jun-25, 14:50
Location: Panama City Beach, FL USA

Stand alone "room in a room" studio build in Orange NSW Australia

#67

Postby gullfo » Sun, 2025-Aug-24, 17:28

q2 - i've used them in a number of studios with excellent results. invest in good quality cameras and a proper video controller so you can minimize the video on your DAW... some folks are sensitive to the (very) slight latency you might experience with cheaper equipment.

q1 - we cannot tell you the secret. lol.

yes the layer of semi-rigid (e.g. OC 703) will preserve a bit more HF than the more open stuff or mineral wool -- but the main advantage is, it keeps the looser stuff in place and provide a good surface for the cloth finish. although a lot of people also use fabric frame systems to stretch their fabric over dacron (or other uphostery type fill) to get a truly professional finish.



gearjunk1e
Full Member
Posts: 112
Joined: Sun, 2021-Mar-07, 19:19
Location: Orange Australia

Stand alone "room in a room" studio build in Orange NSW Australia

#68

Postby gearjunk1e » Mon, 2025-Aug-25, 19:28

gullfo wrote:
q1 - we cannot tell you the secret. lol.


:lol: ...well, at least if the studio design/construction business turns down you can always top up your income doing stand up :lol: :lol:

Seriously, thanks for that and the answer on the window. There is a vibe thing about a window but I suspect that if they had the tech we now have when studios were first built, we may never have seen them appear. Who knows...



gearjunk1e
Full Member
Posts: 112
Joined: Sun, 2021-Mar-07, 19:19
Location: Orange Australia

Stand alone "room in a room" studio build in Orange NSW Australia

#69

Postby gearjunk1e » Fri, 2025-Aug-29, 03:27

So I've been thinking about cameras for my "digital window"...

Seems to me streaming cameras are probably overkill but that 4k security or webcast cameras are candidates

:?: Any wisdom to share here on choices and where to start?

Andrew



User avatar
gullfo
Senior Member
Posts: 793
Joined: Fri, 2021-Jun-25, 14:50
Location: Panama City Beach, FL USA

Stand alone "room in a room" studio build in Orange NSW Australia

#70

Postby gullfo » Fri, 2025-Aug-29, 17:04

generally the high performance camera plus proper switching boxes will produce the best results. typ these are the high res security cameras which physical wiring. one studio i had done in the US had 30+ cameras including outside (security), and inside rooms and CR for person to person collaboration + moveable ones for general views for recording. all controlled via a central switching matrix and routable to all rooms and systems. all cameras were coax to the box, and coax to each local distribution boxes (which also allowed pic in a pic for computer inputs) which output hdmi to the video monitors, and USB to the computers for recording. very very low latency and super crisp even on large monitors + adding computer stuff like timers, lyrics, etc etc.




  • Similar Topics
    Statistics
    Last post

Who is online

Users browsing this forum: No registered users and 20 guests